Forum 2000 watt inverter fuse size - BingWhat size fuse should you use for a 2000w power inverters?

There are 22 rows of recommended cable and breaker sizes.The table can be used to decide what size to use.

The cutoff should be based on the chemistry of the battery.Lifepo4 has 3.0 volts per cell.If you have a 2000 watt inverter, you should consider 24 system volts.I can only combine the lifepo4 in parallel.

A 2000 watt load requires a minimum of 17 Amp at 115 single phase with start up loads factored in.For safe operation, nothing else can be in that circuit.Will a 2000 watt appliance blow a fuse?Was this answer helpful?

Most customer's will use a 150A ANL fuse kit that goes in-line on the positive cable from the power to the battery.The battery cables are AWG.It's best to use 1/0 AWG battery cables on power inverters rated up to 3500 watt.

You can find NEC table 310.17 on the internet.According to the NEC, a #1/0 AWG copper wire with 90c insulation is rated for 260 Amps and has a maximum size of 125%.If you have a rating of 260 Amps, you should be able to get a small fuse to work.

The Renogy 2000W Pure Sine Wave Inverter Charger is a great addition to any RV or trailer solar power system.It will convert DC power to AC and keep the battery bank charged with solar during the day and can switch to generator or shore power at night.

The 2000 Watt Continuous/4000 Watt Peak Modified Sine Wave Power Inverter is not available until April.The high capacity inverter powers handheld power tools, appliances, TV's, stereo and more.

In order to figure out what size fuse you need, we need to refer to ohm's law.The 400 watt inverter is going to run off of 12 volts.400w/12v is 33.333 Amps.Do you know how that works?If you only want to run it at a peak of 350 watt then you will have 29amps.

The above mentioned inverter was installed in the back of my rig.I couldn't help but notice that the 5' power cord is more like 10'.Hopefully it won't be a big deal.I don't know what the size of the positive feed should be.I read it.

The DC cable size is 2000 W.For a cable length of up to 6 feet, the recommended size is 0 AWG.On the input side, a DC fuse is required in addition to the correct wire size.The size of the fuse is 2000 W.The DC side has a maximum rating of 250 A dc.The transformer should be connected.